Boiler drum level control is critical for both plant protection and equipment safety and applies equally to high and low levels of water within the boiler drum.
The purpose of the drum level controller is to bring the drum up to level at boiler start-up and maintain the level at constant steam load. A dramatic decrease in this level at constant steam load. A dramatic decrease in this level may uncover boiler tubes, allowing them to become overheated and damaged. An increase in this level may interfere with the process of separating moisture from steam within the drum, thus reducing boiler efficiency and carrying moisture into the process or turbine
The functions of this control models can be broken down into the following
Operator adjustment of the setpoint for drum level
Compensation for the shrink & swell effects
Automatic control of drum level
Manual control of the feedwater valve
Bump-less transfer between auto and manual modes
Indication of drum level and steam flow
Indication of feedwater valve position and feedwater flow
Absolute/deviation alarms for drum level
The Three main options available for drum level control are
Single element drum level control
The simplest but least effective form of drum level control
This consists of proportional signal or process variable (PV) coming from the drum level transmitter. This signal is compared to a setpoint and the difference is a deviation value
This signal is acted upon by the controller which generates corrective action in the form of a proportional output. The output is then passed to the boiler feedwater valve, which then adjusts the level of feedwater flow into the boiler drum
Notes:
Only one analogue input and one analogue output required
Can only be applied to single boiler / single feedpump configurations with relatively stable loads since there is no relationship between drum level and steam- or feedwater flow
Possible inadequate control option because of the swell effect
Two element drum level control
The two-element drum level controller can best be applied to a single drum boiler where the feedwater is at a constant pressure.
The two elements are made up of the following:
Level Element : a proportional signal or process variable (PV) coming from the drum level transmitter. This signal is compared to a setpoint and the resultant is a deviation value. This signal is acted upon by the controller which generates corrective action in the form of a proportional value.
Steam Flow Element: a mass flow rate signal (corrected for density) is used to control the feedwater flow, giving immediate corrections to feedwater demand in response to load changes.
Any imbalance between steam mass flow out and feedwater mass flow into the drum is corrected by the level controller.
This imbalance can arise from
Blowdown variations due to changes in dissolved solids
Variations in feedwater supply pressure
Leaks in the steam circuits.
Notes:
Tighter control of drum level than with only one element
Steam flow act as feed forward signal to allow faster level adjustments
Can best be applied to single boiler / single feedpump configurations with a constant feedwater pressure
Three-element drum level control
The three-element drum level control is ideally suited where a boiler plant consists of multiple boilers and multiple feedwater pumps or where the feedwater has variations in pressure or flow..
The three-elements are made up of the following
Level Element & Steam Flow Element: corrects for unmeasured disturbances within the system such as
Boiler blowdown
Boiler and superheater tube leaks
Feedwater Flow element: responds rapidly to variations in feedwater demand, either from the
Steam flow rate feedforward signal
Feedwater pressure or flow fluctuations
In order to achieve optimum control, both steam and feedwater flow values should be corrected for density
Notes:
The three-element system provides tighter control for drum level with fluctuating steam load. Ideal where a system suffers from fluctuating feedwater pressure or flow
More sophisticated level of control required
Additional input for feedwater flow required
Enhanced three element drum level control
The enhanced three-element drum level control module incorporates the standard three element level components with the following improvements
The three-element mode is used during high steam demand. The two-element mode is used if the steam flow measurement fails and the module falls back to single element level control if the feedwater flow measurement should fail or if there is a low steam demand.
The drum level can be derived from up to three independent transmitters and is density compensated for pressure within the boiler drum.
Notes:
Tighter control through a choice of control schemes. Drum level maintained on failure of steam or feedwater flow measurements.
This module introduces an additional level control loop